Article 240.5(B)(2), (1),(2) I find this confusing. This part of the article deals with overcurrent protection for fixture wire and states "Fixture wire shall be permitted to be tapped to the branch-circuit in accordance with the following:
(1) 20-ampere circuits - 18 AWG, up to 15m (50 ft) of run length.
(2) 20 ampere circuits - 16 AWG, up to 30m (100 ft) of run length.
Does this mean that the total amount of #18 AWG you could use is 50 ft? Or does it mean that any run cannot exceed 50 ft? Could you feed as many lights as you wanted with #18 AWG fixture whips as long as they are under 50ft?