Do you mean just the enclosure door That pretty much anyone can open? Can just putting a padlock on the enclosure door and calling it accessible by only qualified persons meet 240.6 (B) and (C)?Yes, the adjustments are behind a cover/door that is capable of being sealed thus preventing changing them or at least providing indication they may have been tampered with.
But could simply locking the enclosure door be compliant?There should be a clear cover over the setting dials that can be sealed shut. That's all that's required.
I mean the clear plastic cover on the breaker, like infinity said, which has built in provisions for a sealing wire. The NEC requires the provisions, however it does not require them to be used.Do you mean just the enclosure door That pretty much anyone can open? Can just putting a padlock on the enclosure door and calling it accessible by only qualified persons meet 240.6 (B) and (C)?