This is sort off an explanation.
Arc energy reduction is critical for electrical safety in the
workplace. NEC 2011 introduced an Arc Energy Reduction
requirement for circuit breakers (NEC 240.87) rated 1200 A
and higher. The added circuit breaker requirement has
reduced arc-flash injuries since being introduced by
lowering fault clearing times. The value of 0.07 s for the
new fuse clearing time requirement was chosen to align
with circuit breakers using zone selective interlocking.
However, it should be reinforced that additional
arc energy reduction methods ONLY need to be
implemented if the specified fuse is greater than 1200 A
AND cannot clear the minimum arcing current in less
than 0.07 s.