Does this mean if the main breaker is vertically operated you can not mount a panel up-side down? Does the manufactures okay make it legit? :-?
Does this mean if the main breaker is vertically operated you can not mount a panel up-side down?
I believe so.
Does the manufactures okay make it legit? :-?
How can it?
Yes, unless as noted, with a breaker that can be inverted. Also when breakers are used as switches, up is still on. 404.7.Does this mean if the main breaker is vertically operated you can not mount a panel up-side down?
Nope.Does the manufactures okay make it legit? :-?