msshel0
- Evansville, IN, USA
We are doing a controls/power distribution retrofit on a piece of equipment. I have attached a .pdf of a simplified one line for the equipment. I have a 800A fused main disconnect with a class L Fuse. I have calculated the available fault current @ 48,114A. I'm feeding 2 Panels: a main control panel (MCP) and a power distribution panel (PDP). The MCP has a 600A main with 460.3A of Motor load. The PDP has a 400A main with 104A motor load. The let-through current of the 800A fuse is 17,000A. If I take my motor contributions into account at 6X the full load current, the motors add roughly 3,400A to my fault current. Bringing my available fault current to 21,400A on the load side of the fused disconnect. So, at that point I would think that bringing my MCP and PDP to 25kA would be sufficient. However, since I have 460.3A of motor load in my MCP does that mean my PDP has to be rated > 46030A due to 240.86(C) of the NEC? If that is the case, can somebody explain to me why the motor contribution can only be 1% of the lower rated breaker's rating? Am I mis-applying the code?
Thanks for any help,
Matt Shelton
Electrical Engineer
Matt Shelton
Electrical Engineer