lielec11
Senior Member
- Location
- Charlotte, NC
- Occupation
- Electrical Engineer (PE)
240.86(C) states that series ratings cannot be used where.... and then lists two conditions 1, and 2. Between 1 and 2 it says "and", so am I right to assume that BOTH of these need to be true for it to apply?
I am also a bit confused about 1, which states motors cannot be connected on the load side of the higher (protecting) breaker and on the line side of the lower (protected) breaker. How is that possible? If the motor is fed from the downstream (protected) panel, it will be on the load side of a breaker, not line side. What am I missing? The text in the Handbook doesn't really help me either.
2 seems fairly straightfoward in that the motor loads cannot exceed 1% of the interrupting rating of the lower rated circuit breaker but I have one question. Do I use the regular rating or the series rating? For instance if I have a 10k panel series rated for 65k, which rating do I take 1% of?
I am also a bit confused about 1, which states motors cannot be connected on the load side of the higher (protecting) breaker and on the line side of the lower (protected) breaker. How is that possible? If the motor is fed from the downstream (protected) panel, it will be on the load side of a breaker, not line side. What am I missing? The text in the Handbook doesn't really help me either.
2 seems fairly straightfoward in that the motor loads cannot exceed 1% of the interrupting rating of the lower rated circuit breaker but I have one question. Do I use the regular rating or the series rating? For instance if I have a 10k panel series rated for 65k, which rating do I take 1% of?