Can someone "dumb down" this section so that I might understand it ?? :D

I am inspecting a job where the engineer stating he is installing hardware (a switch ?) on several 3000 amp MB 65k services to address this. I read the Section and tried to disguise the "stupid" written all over my face.
 
The amount of energy that would be released during an arc flash event depends mostly on two things: the available fault current and the amount of time it would take the upstream OCPD to terminate the event when that much current is flowing. The intent of this NEC section is to reduce the hazard to a worker by one of several approved means.

But let’s back up a step. It turns out that reducing arc flash energy and providing for selective coordinate are contradictory goals. If you want a breaker close to the fault point to trip before your main breaker trips, then you slow down the trip mechanism on the main breaker, so as to give the downstream breaker time to trip first. However, that will mean that if the main panel is open for inspection, and if an arc flash event begins, it will take the main breaker a long time before it reacts. That will allow for a high value of arc flash energy to be released.

One way to mitigate this possibility, and this is what I think the engineer is proposing, is to install a “maintenance switch.” The worker will turn this switch from “normal mode” to “maintenance mode” before opening the switchboard. What this does is to reset the main breaker’s trip characteristics, so that it would trip faster in the event of a fault. Thus, a lower amount of arc flash energy would be released. This switch will have the side effect of disabling the selective coordination arrangement, since on a fault further downstream it is possible that the main breaker will trip before the feeder or branch circuit breaker. That is the risk that you accept, in order to gain the benefit of a lower risk to the worker during an arc flash event. For this reason, the code requires that the maintenance switch be accompanied with an indicating light, so that the system is not inadvertently left in a condition that has selective coordination disabled.
 
Can someone "dumb down" this section so that I might understand it ?? :D

I am inspecting a job where the engineer stating he is installing hardware (a switch ?) on several 3000 amp MB 65k services to address this. I read the Section and tried to disguise the "stupid" written all over my face.

For coordination purposes, with down stream equipment, some people set adjustable trip breakers to their maximum settings. These high settings may mean the breaker does not respond quickly to arcing faults (this is also why GF protection is required on these devices). The slow response may result in high levels of arc fault incident energy (AFIE).

Basically, this NEC section requires that a circuit breaker have a method that allows the end user to lower the AFIE at downstream equipment even if it means sacrificing coordination.
 
Can someone "dumb down" this section so that I might understand it ?? :D

I am inspecting a job where the engineer stating he is installing hardware (a switch ?) on several 3000 amp MB 65k services to address this. I read the Section and tried to disguise the "stupid" written all over my face.

I'm so "dumb" I can't even find 240.87 in the 2008 NEC!:happyno:
(Gus and I are under the 2008)
 
I'm so "dumb" I can't even find 240.87 in the 2008 NEC!:happyno:
(Gus and I are under the 2008)

Despite TN still being on the '08 (later this month the powers that be are going to discuss that), the job is being installed per the '14.
 
Thanks. I'm clear now on the procedure. On what premise would such a switch be installed ? To reduce the category of PPE necessary when "hot" work had to be performed ?
 
On what premise would such a switch be installed ? To reduce the category of PPE necessary when "hot" work had to be performed ?
Yes. But I think it is more appropriate to say that the purpose is to reduce the risk of injury, and to reduce the seriousness of such an injury, to the worker.

 
Despite TN still being on the '08 (later this month the powers that be are going to discuss that), the job is being installed per the '14.

How can it be installed under the "14"? Are you obligated to inspect it as such?
Only thing I can think of would be stamped drawings by a "PE"?
 
How can it be installed under the "14"? Are you obligated to inspect it as such?
Only thing I can think of would be stamped drawings by a "PE"?
We are advised our job is to assure it meets minimum Code, in TN case '08. Anything above and beyond that is certainly permissible.
 
We are advised our job is to assure it meets minimum Code, in TN case '08. Anything above and beyond that is certainly permissible.

Understood.
How would you handle a situation where something is not allowed under current adopted code that is now allowed in a more recent code, if an electrician used the more recent code?
 