I am looking at installing a PV system onto a 240 Delta High-Leg (center ground) service. I have found a single phase inverter that can be connected to two of three phases with this type of service and I'm planning on using three inverters to do a balanced backfeed. I need to calculate out my max line currents to size the equipment between the inverter combiner panel and the utility tie-in.
Are all three phases for this type of service 120 degrees out of phase, similar to a 208/120 or 480/277 where my max line currents would be the inverter current multiplied by the square root of three? This was my assumption until I started googleing the subject and read somewhere that the two "bottom" legs that have the neutral center grounded are 120 degrees out of phase similar to a 240 split phase.
Can anyone clarify on the phase angles measured between L1 & L2, L2 & L3, and L1 & L3? And how to calc out the max line currents when I have three single phase inverters tied to this service in a delta formation? Note this type of tie-in requires the inverter to operate WITHOUT the neutral, which is an acceptable application for the inverter according to the manufacturer.
Are all three phases for this type of service 120 degrees out of phase, similar to a 208/120 or 480/277 where my max line currents would be the inverter current multiplied by the square root of three? This was my assumption until I started googleing the subject and read somewhere that the two "bottom" legs that have the neutral center grounded are 120 degrees out of phase similar to a 240 split phase.
Can anyone clarify on the phase angles measured between L1 & L2, L2 & L3, and L1 & L3? And how to calc out the max line currents when I have three single phase inverters tied to this service in a delta formation? Note this type of tie-in requires the inverter to operate WITHOUT the neutral, which is an acceptable application for the inverter according to the manufacturer.