I got a Septic pump control box and I ran the system with a multi wire circuit 12 thhn/thwn. I realized that tapping off the RV pedestal feeders the lugs are not rated at 90% Here my original question about that.
calculating-additional-load-on-feeder-for-rv-pedestals.2574311
So instead of doing the Polaris taps on the meter , Or pulling out the 12 and pulling in 10 thhn/thwn pipe. does 240.g apply to the feeder to the control box circuit breakers. I think It applies I see nothing that says I can't do that.
calculating-additional-load-on-feeder-for-rv-pedestals.2574311
So instead of doing the Polaris taps on the meter , Or pulling out the 12 and pulling in 10 thhn/thwn pipe. does 240.g apply to the feeder to the control box circuit breakers. I think It applies I see nothing that says I can't do that.