Have a 240v circuit (Red, Black, White, Ground) running between main panel 30amp breakers and subpanel (103 ft away using a buried cable (#4 wire) running through attic and conduit outside to sub-panel). Vltage was OK until a lot of rain which could have cause some swelling of infrastructure or ground sepage. Did a visual check for leaks or wet spots and found none. Also dug up duried run and found no damage or wetness.
Issue is that one hot leg is 123v while the other is 45v instead of 123v. Disconnected Red, Black, and White legs and performed an Ohms test. Got zero between Red & Black and zero also between white and red and white and black.
Disconnect Red at both ends and checked voltage. Black was 123v and Red 45v. Also did Black test with same results. I had also checked all connections for corrorsion and found none and tighten all conections... no voltage change. With the circuit off, I got around .28v and .19v on the legs.
I verified my testing equipment on another circuit too.
Anyone got a good idea what could be causing the voltage drop/bleed and the best way to correct it?
Thank you.
Issue is that one hot leg is 123v while the other is 45v instead of 123v. Disconnected Red, Black, and White legs and performed an Ohms test. Got zero between Red & Black and zero also between white and red and white and black.
Disconnect Red at both ends and checked voltage. Black was 123v and Red 45v. Also did Black test with same results. I had also checked all connections for corrorsion and found none and tighten all conections... no voltage change. With the circuit off, I got around .28v and .19v on the legs.
I verified my testing equipment on another circuit too.
Anyone got a good idea what could be causing the voltage drop/bleed and the best way to correct it?
Thank you.