rt66electric
- Oklahoma
I was asked to bid on adding an additional 3p circuit to panel. I found a 240v 3ph panel box and breakers being fed by a 100a 480v 3ph
It was a mismashed area some new eqiupment and some old. This sub-sub panel is fed by a 100a breaker off a federalpacific sub panel.
The incoming wireing consists of 1 1/2 EMT w/ (3) #2 maybe #4 AWG TW conductors without a ground conductor. The conduit/j-box also carries a set of (3) #10 condutors feeding a nearby disconnect.
This Is a power only panel no neutral
If I replace the panel should I ??
A- replace all of the conductors and add a green wire?
B- replace the panel useing existing conductors and call it good??
C- replace the panel useing existing conductorsand add a supplementary ground wire to overhead building steel??
My bid is competing w/" Mr. lowball bare minimum, its working long enough to get my check"
Management is aware of "Safety Hazard" ,but will look at numbers. If apples are cheaper than oranges, they will take the apples.
It is difficult to convince mgmt that added price to do the job correctly is necessary , as opposed to the "I can replace it with a new shiny panel price"