I've got a request for a single phase trans. 120/240 v to 120/240 v wired like the attachment.
Why would anyone even need a trans. in this case? What would the be the safety issues if the neutral was not grounded
on the secondary side? I don't get it.?
 

Attachments

  • 240 TO 240 DIAGRAM.pdf
    85.2 KB · Views: 1
I've got a request for a single phase trans. 120/240 v to 120/240 v wired like the attachment.
Why would anyone even need a trans. in this case? What would the be the safety issues if the neutral was not grounded
on the secondary side? I don't get it.?

IMHO... It could have been added as extra impedance in a system, or to act as a filter.
 
If the input is at the top, then the transformer is taking a possibly floating 120V input and producing center tapped 120/240.
There could be a variety of reasons to do that.
One would be to get a balanced 120/240 from a single ended 120 input without using an autotransformer (for some unknown reason).
The X to Y input is NOT 240.
 
That diagram doesn't indicate what connections you are going to use, so why would anyone assume anything? Could be that they just want a reliable source of 120V from a 240V supply. If for example it's in a control panel for a machine that might be connected to a 120/240 3 phase 4 wire delta system, which terminal you tap off of to try to get 120V without a CPT can result in you getting 208V and frying your controls. So by specifying a CPT wired as 240V primary, 120V secondary, the phases used to tap to the primary become irrelevant. That's the most common reason by the way.
 
That diagram doesn't indicate what connections you are going to use, so why would anyone assume anything?
I see the diagram as showing a parallel connection of the input windings on the H side and a series connection (with center tap) of the secondary windings on the X side. Given that the transformer is rated as 120/240 to 120/240, what more were you expecting to see?
 
I see something in this that makes no sense to me.

The transformer is suppose to be 120/240 to 120/240.

Ok' we can't drive the two 120 volt windings in parallel with 240
volts Right?

What voltage are X and Y

Where is this neutral coming from, shouldn't the neutral be H1 and H3 or H2 and H4?



Or is this Transformer suppose to be a 240/480 to 120/240?

Forget about that I thought of two more reasons it could be used this way

1.-They just have one circuit free in there panel or they want to use a 1 pole breaker.
2.-Or as Jon said if they wanted to use this to drive a 120/240 Log cabin service with a 120 volt Generator.

But you need to do some work on the H side.
 
I used one to power the active filter for my European Bose-901 speakers when I brought them back to the states. The filter needed 240VAC which was hard to find in a receptacle in rental property. Ditto for EU sewing machine, apartment sized refrig., waffle iron, steam iron, ....

It's just a transformer.
 