Hi, I've just moved my business into an older building and the electrical service is 240 volt delta. I have 2 CNC machine I need to hook up with a total load of 45 amps @ 480 volts. Both have VFDs driving their spindles. The electrician is proposing reverse feeding a 480 delta x 240 delta stepdown transformer. I asked him about corner grounding and he no, so he's proposing running it as an ungrounded delta system.
This sounds kind of dangerous, since in the event of a ground fault it becomes an ad-hoc corner grounded system and the breaker doesn't trip. Is there a simple way to add ground fault protection?
I've also considered intentionally running it as a corner grounded delta system. The problem there is that I'm finding differing opinions on whether the VFDs can tolerate it. Some manufacturers recommend disconnecting the MOVs, some drives don't provide for that, and some people even say that if the component spacing is right in the drive it's no big deal.
The third option would be ordering a custom transformer which will convert the 240D into 480Y. This seems like a much better solution, but it would cost an extra thousand dollars. What do you guys think?
This sounds kind of dangerous, since in the event of a ground fault it becomes an ad-hoc corner grounded system and the breaker doesn't trip. Is there a simple way to add ground fault protection?
I've also considered intentionally running it as a corner grounded delta system. The problem there is that I'm finding differing opinions on whether the VFDs can tolerate it. Some manufacturers recommend disconnecting the MOVs, some drives don't provide for that, and some people even say that if the component spacing is right in the drive it's no big deal.
The third option would be ordering a custom transformer which will convert the 240D into 480Y. This seems like a much better solution, but it would cost an extra thousand dollars. What do you guys think?