heymitduh post #1 said:
OK, with 120 V you have a hot and a neutral (return path). Where is the return path on a 240 V circuit where you have 2 hots and an equipment ground?
heymitduh post #4 said:
Why do you get different amperage readings on the two legs of a 240 V circuit? This is a lot of theory and I don't need it to perform my job. Just interested.
heymitduh post #6 said:
The reason that I said is because I've experienced it. I just went down in my basement and tested the amperage on my electric water heater. Variation of close to .5 amp between the two "hots" (ungrounded conductors) And I recall the same situation when I hooked up my neighbor's welder. 50 A two pole that varied about 2 amps between legs.
heymitduh post #9 said:
It's a Fluke T5-600. So you agree that I should get the same amperage reading in both legs and the reason I don't is due to induction? Same as "stray magnetic fields"?
I would like to suggest a different possibility than stray magnetic fields.
Since your load is 240v and you're taking hot to ground readings, I believe that your readings have nothing to do with your 240v water heater itself. . For the sake of conversation, I'll refer to the 2 hots as black and red.
I believe what you're reading on the black is the voltage drop across 3 different things that are in
series, the water heater black and green wires, the black and green wires of a nearby 120v circuit [thru the panel], and the nearby 120v load itself.
I believe that the reading on the red is the voltage drop across 3 different things that are in series but it’s
not the same 3 things as the black phase. . The reading on the red is a series voltage drop reading across, the water heater black and green wires, the black and green wires of a nearby 120v circuit that’s a
different circuit than the one read on the previous reading for the black phase, and that nearby 120v load itself.
Everything being equal, the voltage to ground would be the same on each leg but the 120v circuits that “snuck” into your readings are probably very different from each other with different wire lengths.
I would be curious what kind of reading you would get if you turn every single breaker in the building off except the water heater 2 pole. . That would isolate out the other building loads. . If you take that reading post the result.
David