speedypetey said:A 240v GFI breaker works exactly the same way, only it monitors both 120v and 240v at the same time.
You can have an imbalance in the two legs of the breaker because the neutral will carry it. The GFI knows this.
What is your point???zog said:I think you are talking about a GFCI, not a GFI.
speedypetey said:What is your point???
If you are being anal about it, YES, you are correct. The proper term is GFCI. GFI is easier to write and generally accepted. I classify it along with "neutral" instead of grounded conductor and "ground" instead of grounding conductor.
zog said:" Guess thier plant elecricians didnt think there was a difference either.
I'm just saying. :grin:zog said:"Apples" is also easier to write (1 charlater shorter) than "Oranges".
The easiest way to visualize the operation of a GFCI is to picture a clamp-on ammeter. If you clamp around the hot and neutral on a 120v circuit, you'll get a reading of zero (assuming no ground fault ) This is because the current going each way is equal and cancels the other out.KRG9729 said:I don't understand how a 3 wire GFCI circuit is supposed to work. I know on a 120 volt circuit it monitors the current between the hot and neutral and shunt trips when there is slight imbalance. Any help would be appreciated,