can someone explain how a 240 volt gfci circuit breaker is going to work on a pump motor for a swimming pool?
Steve Brady said:can someone explain how a 240 volt gfci circuit breaker is going to work on a pump motor for a swimming pool?
stickboy1375 said:Not directed at the OP, but anyone want to guess why this question is a hard one? And is asked quite often.
Steve Brady said:the pool pump operates at 240 volts, no neutral on the pump , currents flow from the cb to device the gfci will monitor the current supplied but will not monitor the return currents on the neutral so the question still is how will someone have gfci protection on the pool pump motor (required)
Steve Brady said:the pool pump operates at 240 volts, no neutral on the pump , currents flow from the cb to device the gfci will monitor the current supplied but will not monitor the return currents on the neutral so the question still is how will someone have gfci protection on the pool pump motor (required)
iwire said:When a GFCI is protecting a 240 volt circuit it monitors the current on both hots, as long as they are within about 5ma the GFCI will not trip.
Dennis Alwon said:Why does the neutral need to be connected on the breaker if it is only monitoring the current on both legs of a circuit without a neutral load. That may be what the op wants to know. I don't have the answer but it needs to be connected.
stickboy1375 said:My guess is that the electronics inside the breaker require it.
Dennis Alwon said:Brilliant Stickboy--:grin:. Yes that was sarcastic--![]()
M. D. said:Hey ,.. I just thinking of Andy and his festival gfci issue .. if the 2pole GFCI only had current on one phase could,..that be causing his gfci to trip ....??? just thinking out loud and I know it is the wrong thread ,.. maybe a current is being created in the phase with no load??
M. D. said:Hey ,.. I just thinking of Andy and his festival gfci issue .. if the 2pole GFCI only had current on one phase could,..that be causing his gfci to trip ....??? just thinking out loud and I know it is the wrong thread ,.. maybe a current is being created in the phase with no load??
andy said:One other item of note that sort of raises a red flag with me is that the manufacturers wiring diagram has all of the modules on one leg of the 240 V circuit (the other leg is used for additional modules on larger systems) and am wondering if this could cause any problems with the gfci tripping. Would an imbalanced load on a 2 pole gfci make it trip? I don't think so, but I'm trying to think of everything.
M. D. said:Why is that
Dennis Alwon said:If the gfci is feeding a MWBC then would that happen. There would almost always be a difference in current between phases. No?
Dennis Alwon said:MWBC- common neutral--suppose phase A is running a circuit at 13 amps and phase B draws 10 amps. Are you saying that would trip a dp gfci? I thought a dp gfci would work on a MWBC