I am being told light fixtures rated for 120-277V can also operate at 240V, single phase 2-Hots? Is that correct? I am getting conflicting info.

Dan Craven
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Wut?

Seems like they should label “120/277” instead of “120-277” then.

Never knew this.


Sent from my iPhone using Tapatalk
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Well the link to the other thread was about electronic, fluorescent ballasts. Old school HID ballasts could definitely be hooked up 240V but nobody uses those anymore. We need to know more about the OPs lights before a real answer can be given.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Well the link to the other thread was about electronic, fluorescent ballasts. Old school HID ballasts could definitely be hooked up 240V but nobody uses those anymore. We need to know more about the OPs lights before a real answer can be given.


120-277 would be electronic, 120/277 and 120/208/240/277 would be magnetic multi tap.
 