240 volt loadcenter wired 120
Ed Carr said:
In post #9 hardworking refers to a special neutral switching breaker.
Can anyone please tell me what that is. Not a gfi apparently. Thanks, Ed
It is a breaker that has a neutral wire coming out of it that is connected to the neutral bar and then you connect your circuit neutral to the breaker beside the ungrounded conductor. I use them to satisfy 514.11. You are correct, it is not a GFI.
A single pole takes up 2 spaces in the panel and a 2-pole takes up 3 spaces. The single-pole usually cost about 2-3 times as much as a standard 2-pole breaker.
The funny part, if true, is that I've heard in Canada, it is a code violation to do this.
UL Panelboard Marking Guide '07
page 5
Voltage Rating
6. The basic voltage markings must be visible without disturbing wiring and other interior parts. . A panelboard designed and intended for use only on a supply circuit involving two different potentials (for example, 120/240 volts, three-wire; or 208Y/120 volts, three-phase, four-wire) is so marked.
It would be my guess that the reason for the restriction and the use of the word "only" is because of concern with the MWBC situation. . There are electricians everywhere that would land the hots on side by side breakers and not give it another thought. . Doubled neutral currents is a huge concern.
You'll have to check the panel label to know for sure but I hope UL has handled this one properly and is preventing legal installations of a single hot to multiple bus bars. . I'm sure it will still continue to be done even if not legal. . But I hope their panel marking is keeping it out of legal installations.
David
georgestolz said:
Stupid question: If it were illegal to use a panelboard as such, how would we make use of 690.10(C)?
Very nice find George, but wouldn't that imply it would not be legal in situations other than specified in art. 690.10(C). :confused:
No, it's an express permission to do so in that circumstance. It is not a prohibition from doing it in other circumstances. (90.5(B))