Do 240 volt recepts on a kitchen countertop have to be GFCI protected?
No, but they may be prohibited if the appliance is under a certain wattage.
thanks, I didnt think they needed to be, I overheard a guy insisting that it was required.
210.8(A) is the general location in the NEC that you will find the information as to which type of receptacles are required to be GFCI protected. For Pools it is in 680.
If not in "dwelling units and guest rooms or guest suites of hotels, motels, and similar occupancies" it would be allowed.If the 240 was and probably is 120 to ground, then would it be allowed?
Probably will not happen until this fall. What is really interesting is the IRC (Indiana Residential Code) will no longer match the IEC (Indiana Electrical Code). If you wire to the IEC and are written up for an IRC violation, you will have to let the inspector know that you did not wire to the IRC. Of course, the opposite can happen as well.. . . Indiana is changing over to 2008 . . .