I want to step up from 240 to 480 volt 1 phase can I use a 3 phase transformer? ( I have 240 v single phase I want 480 v single phase)
Why would you want to use a 3 phase transformer?
Well, it might be interpreted as a violation of article 110...I did not say I want to. I asked if it work. and be code compliant .
Except that you would have the additional magnetizing current for the other two coils in series across the coil you connected.First to get 480/240 you would need a delta - delta transformer (at least if using something sort of common stock)
But if using delta-delta you could just hook up one phase and effectively only have a single phase transformer with about a third of the kVA capacity of the nameplate.
Ok, you would need to disconnect at least the tie between the other two phases - if you can get to a place where they are connected. When I posted that I was thinking more so about how the POCO's typically build delta banks out of single phase transformers, but since those often are configured wye on the primary side I wasn't really on the right path anyway.Except that you would have the additional magnetizing current for the other two coils in series across the coil you connected.
If you happen to have a suitable three phase transformer on hand, and do not care at all about inefficiencies, it would work.
A wye-wye would not have that problem.