wireman3736 said:
I don't believe I have ever seen an ungrounded system in my area?
I only remember running into it once when I was still an apprentice.
two questions come to mind, is this type of installation still allowed
Yes.
and if it is what would be the benefits of this type of system.
The benefit is that when a circuit conductor shorts to ground none of the over current devices open.
If you have a factory you don't want a ground fault in a circuit shutting down equipment necessary for production.
However, there should be fault indicators and a people on site who know what the indicators mean and how to get the problem resolved.
With the correct tools and skill the ground fault can be located and repaired with little to no downtime.
If the fault is not corrected the next fault on an opposing phase will open at least one overcurrent device and will cause downtime.
I believe that High-Impedance Grounded Neutral Systems are becoming more popular than ungrounded delta but I have no hands on experience with either.
Don't bet your life on the above, it comes mostly from what I have read on the forum.