240V/1PH equipment connected to 208V/1PH circuit?

mdgardner

Member
Location
Roswell, GA
Occupation
Electrical Engineer
I have a client that has purchased a piece of equipment that is rated 220-240V, 10.8A with a Nema 6-20 plug. (see attached picture of nameplate). The building has a 120/208V system. What happens if I connect this at 208/1 or should I provide a 208:240 transformer?
 

Attachments

  • IMG_6162.jpeg
    IMG_6162.jpeg
    1.1 MB · Views: 19
  • IMG_6163.jpeg
    IMG_6163.jpeg
    694.6 KB · Views: 18

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Looks like a resistive heater load so it just will have a lower output on 208 volts.
 

kwired

Electron manager
Location
NE Nebraska
Looks like a resistive heater load so it just will have a lower output on 208 volts.
Which possibly could mean going with a higher rated unit if the lower output won't be acceptable, or stepping up voltage.

mdgardner, you could use a buck/boost transformer which only would need sized per the boosted VA needed instead of one that needs to carry full VA of the load if you must use this one at 240 volts to get desired wattage.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Nameplate says 2600W @ 240V so it will probably be 1952W @208, if its controled by a thermostat it should be fine on 208.
 