Not driven by a vfdA step-down transformer will do it. A bigger issue may be running 60Hz US motors on 50Hz.
There are a lot of "It depends" here, motor size, type, the load, whether they're connected across-the-line or driven by a variable freq. drive, etc.
I agree with this. 240 Volts @ 60/hz is 4 hz/rpm at 200 volts 50 hz you would get the same ratio of 4.more than likely you can step your 415 50 Hz to 200 V and run the motors on that. They will run slower than designed and offer less torque, but that might be acceptable.
otherwise you need some other solution, maybe some VFDs. it is hard to know what your situation is so hard to give you any advice that is not conditional on a lot of things we don't know.
Link please?With some searching, you'll find some threads here about running 50Hz motors on 60Hz and 60 on 50; these will explain things like the differences in torque, power consumption, heat, etc.