240V 3Ph Generator Grounding

Status
Not open for further replies.

ERolla95

New User
Location
Missouri
Occupation
Engineer
I have a project where they have 2 separate 240V 3phase services feeding the building. One is 200A, 3 wire, corner grounded feeding HVAC loads and the other is 400A, 4 wire, neutral grounded, high leg. They want to feed them both from a single 240V 3phase generator feeding separate transfer switches for each service. I have not run across this before and I am trying to wrap my head around how to ground these properly. Is this possible or will they need separate generators? Any help or advice is appreciated.
 
It's not possible to both corner-ground and center-tap ground the same coil of a generator at the same time, it usually lets the magic smoke out :ROFLMAO: . If you use two 4-pole transfer switches and interlock them, you could put the bonding jumper after the TS and leave the generator to float unless a TS is closed).

Or you could corner-ground the generator, use two transfer switches, and put a transformer after one of them to get the high-leg delta; ground that as an SDS.
 
Kinda odd the poco built two different banks for such a small service.
Unless they used single phase panelboards on the corner grounded delta service, it would probably be the easiest to have the poco re-connect the bank to a four wire, and change the bond at the service (adding a neutral to the service disconnect)
 
If the transformer is changed to a center tapped unit the entire system, it feeds, may need to be rewired.

A corner grounded system may be employing 2 pole protective and switching devices. If it was installed correctly, per code, the grounded conductor would be white

As Zbang said, connect the generator as a 4 wire delta and then provide a separate transfomer to feed the 3 wire system.
 
... A corner grounded system may be employing 2 pole protective and switching devices. If it was installed correctly, per code, the grounded conductor would be white. ...
When was the building wired? This was common practice during WWII, as a wartime expediency. However many contact sets you could make in a day, you could make 50% more contactors if they're only 2-pole.

If it was wired 80 years ago, it was likely with cotton-over-rubber insulation and it might be very difficult to distinguish the colors today. And that's assuming they didn't mix & match colors as another wartime expedient.
 