What are the issues of using a 240v primary step up transformer to 480v using a 120/208 service.. client want me to hook it up. The lowest I can change taps is 214v inside the unit..
Other than low voltage, no problem.
Sounds a bit uncommon to have a 214V tap on a 240V primary, I'd suggest posting the transformer nameplate.
Jon
If your input is about 208V, you only get 416V in the output! Please check if your service voltage can be raised a bit to 220V (I doubt that can be done but just maybe) to arrive at a 440V output. I have seen lots of 480-volt motors do well when supplied with 440V.What are the issues of using a 240v primary step up transformer to 480v using a 120/208 service.. client want me to hook it up. The lowest I can change taps is 214v inside the unit..
Thanks for getting back at us and providing the closeout!Wow.. this really works.. thank to everybody that replied..
so i did connect the unit. My service is 120/208 3 phase.. I get 208 phase to phase on all 3.. I was getting 450v on the secondary side.. Changed the taps to the 214v input option.. Only had 5 this was the lowest tap to match voltage input... After this change voltage increased to 465 -470 v on the secondary side..
The unit plate reads 240-480.. I called the manufacturer and explain the situation and said it was the wrong transformer and that i should get a 208-480 transformer..
I explain it to customer and hes ok.. Machines are working fine.. I just want to make sure or understand if 208v to transformer will damage it somehow..
What does voltage look like when loaded?Wow.. this really works.. thank to everybody that replied..
so i did connect the unit. My service is 120/208 3 phase.. I get 208 phase to phase on all 3.. I was getting 450v on the secondary side.. Changed the taps to the 214v input option.. Only had 5 this was the lowest tap to match voltage input... After this change voltage increased to 465 -470 v on the secondary side..
The unit plate reads 240-480.. I called the manufacturer and explain the situation and said it was the wrong transformer and that i should get a 208-480 transformer..
I explain it to customer and hes ok.. Machines are working fine.. I just want to make sure or understand if 208v to transformer will damage it somehow..