240v debate....

Status
Not open for further replies.

stickboy1375

Senior Member
Location
Litchfield, CT
I wanted to run a pump at 240v vs 120v, for obvious reasons, voltage drop, wire size, etc. But... I get this a lot from people, 240v is more dangerous. So I'm looking for a better way to explain to people that its just as safe as a 120v circuit but with better benefits.
 

iwire

Moderator
Staff member
Location
Massachusetts
Well both are 120 volts to ground so the chances of them getting a 240 volt shock without them actually opening a j box or enclosure first are pretty remote.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Any rationale you present will probably be accepted only after they accept the fact the the world is not flat.
Explain to them that "220 wire is cheaper" and go on with life :D
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Explain to them that 240 volts will use less energy (kWh), thereby saving them more money in the long run...
(I^2R)
As far as being safer, do they make a habit of playing with live circuits?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Explain to them that 240 volts will use less energy (kWh), thereby saving them more money in the long run...
(I^2R)
As far as being safer, do they make a habit of playing with live circuits?

Why would it use less energy. The wattage is the same and that is what you pay for.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Actually they will use the same amount of energy minus any loss from voltage drop using the lower voltage, if it is a short run, then it would be a wash.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Why would it use less energy. The wattage is the same and that is what you pay for.

Calculate the I^2R using the same size wire.
The resistive losses are less in a 240 v circuit that is using 1/2 the current to do the same work as a 120 V circuit.
It isn't enough to notice in a power bill...
 

iwire

Moderator
Staff member
Location
Massachusetts
Calculate the I^2R using the same size wire.
The resistive losses are less in a 240 v circuit that is using 1/2 the current to do the same work as a 120 V circuit.
It isn't enough to notice in a power bill...

Of course but you would not use the same size wire becuse the current would be half or twice as much depending on which way you are going
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Of course but you would not use the same size wire becuse the current would be half or twice as much depending on which way you are going

What if the amps at 120 and 240 was less than the rating of a 14 guage wire?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Calculate the I^2R using the same size wire.
The resistive losses are less in a 240 v circuit that is using 1/2 the current to do the same work as a 120 V circuit.
It isn't enough to notice in a power bill...
But you statement was to tell the customer they will be saving money

Hv&Lv said:
Explain to them that 240 volts will use less energy (kWh), thereby saving them more money in the long run...
 

Rick Christopherson

Senior Member
You may not notice it in a power bill, but the savings will still be there. :happyyes:
If the amperage is low enough that either configuration will use #14 wire, then the difference in the losses will also be incredibly trivial. Blindly stating this as though it was something of some importance is the reason why we have so many DIY'ers suggesting that they should rewire all of their motors to 240 volts, because their "electrician" friend told them they will save money, or the motor will run cooler, or the motor will have more power. :slaphead:
 

Besoeker

Senior Member
Location
UK
Yes. But body parts would have to contact both lines simultaneously.
True. And it would also need the person electrocuted so to have been fiddling around with live wires.
But yes, 230/240V is more dangerous if you work on it live. Most people don't.
In UK, domestic supplies are almost always single phase, 230V, 50Hz.
Phase to neutral from the from a star (wye) secondary of a distribution transformer.
Appliances are all 230V, 50Hz. From light bulbs to electric cookers.
Deaths from electrocution are, fortunately, rare.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
If the amperage is low enough that either configuration will use #14 wire, then the difference in the losses will also be incredibly trivial. Blindly stating this as though it was something of some importance is the reason why we have so many DIY'ers suggesting that they should rewire all of their motors to 240 volts, because their "electrician" friend told them they will save money, or the motor will run cooler, or the motor will have more power. :slaphead:

My original comments at the beginning of this thread wasn't meant to be taken so seriously as to start an argument about the savings, however trivial, of 120 versus 240.
The comment I made was actually meant to be taken as lightly as Auggies comment: Any rationale you present will probably be accepted only after they accept the fact the the world is not flat.
Explain to them that "220 wire is cheaper" and go on with life.


I am not "blindly" stating anything. I learn much from this forum, and expect to learn much more. I didn't expect to be attacked for for a statement made in jest.
Lighten up.
 

Rick Christopherson

Senior Member
My original comments at the beginning of this thread wasn't meant to be taken so seriously as to start an argument about the savings, however trivial, of 120 versus 240..........
I understand. However, after stating it once, you defended it several times. That leaves the perception that it is not quite so off-hand at that point.

Please understand my perspective. From as far back as the early days of the internet, I have been inundated with questions and comments about reconfiguring motors for 240 volt operation. Not all of these come from DIY'ers. Some of the most adamant arguments have come from professional electricians that have cited their lengthy credentials as preface to their arguments. It's not the type of viewpoint that would last long on a forum like this one, but nevertheless, it does exist among some professionals. All it takes is one off-hand mention from a professional to a DIY'er, and it suddenly becomes a near insurmountable piece of misinformation.
 