Mike01 said:In a 240∆/120V-3?, 4W system the voltage ?B-N (high leg) measurers 208V. How is this calculated? And what would happen if you connected a 480∆-3? and provided a center tap ground? What would your voltage be on that system?![]()
Mike01 said:So how does that same theory work for three phase 208v if C=208 than A=169.9? not 120?
When voltages are represented as vectors (or phasors as some prefer to call 'em), i.e. where length equates to magnitude and direction correlates with phase angle (the point in the reference cycle where [positive] peak voltage of secondary waveforms occurs), one can use geometry and trigonometry to determine voltage and phase angle from any two connection points.Mike01 said:My mistake I should have re-worded my second question why is it 90 degrees in a delta? what would it be in a Wye 60?
How so? ...given VAN as the reference voltage.rattus said:Nice diagram Smart, but the arrows are pointing the wrong way.
Smart $ said:How so? ...given VAN as the reference voltage.
Also see "Positive and negative angles". Using negative angles is actually more correct in phase angle description than is positive angles, since B and C phases do lag A phase.
On positive and negative angles I emphasize the latter part of the following passage:rattus said:Because, for example, a phasor @ 0 degrees points due east. Not a matter of positive/negative. If you specify the angle, you should point the arrow in that direction.
The given line in my diagrams are the ones noted to be at 0?.A convention universally adopted in mathematical writing is that angles given a sign are positive angles if measured counterclockwise, and negative angles if measured clockwise, from a given line. If no line is specified, it can be assumed to be the x-axis in the Cartesian plane.