240V delta

Merry Christmas

jeff motta

Member
Location
nj
Occupation
electrician
I am looking for some advice, I have a client who wants to add a power panel for 120v receptacles around the plant, I found a spare 200A 3phase breaker available, but the service is 240V delta. I plan to come off the spare 200a breaker from the 240v delta panel, install a 75KVA 240 delta to 208v/120v wye transformer to feed the new power panel, I wanted to know if there are any specifics as to breaker/fuse sizing.

Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Art 450 for transformer protection (normally 125%) then Art 240 for conductor protection and Art 250 for grounding.
 

jeff motta

Member
Location
nj
Occupation
electrician
If its center tapped that would be what I call 4 wire.
Why not use the center tap and just do a single phase 120/240 panel for the 120V loads?
I could be wrong about the center tap, this is the older service now fed from the new 480 service, they have a 300kva 480v delta to 240v/120v delta transformer feeding a main 240 3phase 3wire distribution panel, then out to the older service. All of the older main service is fed only with 3phase 3wire (no neutral) and its original labeling says 3pahse 3wire, so again I may be wrong, that's why I'm here asking for help. I do like your suggestion.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I could be wrong about the center tap, this is the older service now fed from the new 480 service, they have a 300kva 480v delta to 240v/120v delta transformer feeding a main 240 3phase 3wire distribution panel, then out to the older service.
Check your 240v delta line-to-neutral voltages. You should have two at 120v and one at 208v.
 

jeff motta

Member
Location
nj
Occupation
electrician
So, you have two 120v L-N lines now. How large is your expected 120 loading?

If relatively small, I agree. Just install a 1ph 120/240v panel from your existing service.
Yes, A phase and C phase to ground = 120v B phase 208V to ground. This panel will be for 120v power, fans, lights, power for small machines possibly.
 

jeff motta

Member
Location
nj
Occupation
electrician
Then you're golden. Install a 1ph panel using A, N, and C, ignoring B.
Thats what I originally wanted to do, but when I opened the main panel, it lacks the neutral. All of the older 208v/120v panels have a 240v delta to 208v/120v transformer feeding the 208v120v panels.
 

jeff motta

Member
Location
nj
Occupation
electrician
Can you add one? Can you find the transformer's secondary neutral?
it would be too much work; they have parallel 4/0 - 3 conductor tray cable feeding the old service, that's why I am looking for info on sizing for the 240 delta to 208v/120v wye transformer set up.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
it would be too much work; they have parallel 4/0 - 3 conductor tray cable feeding the old service, that's why I am looking for info on sizing for the 240 delta to 208v/120v wye transformer set up.
The transformer protection rules are in Table 450.3(B) and the secondary conductor rules in 240.21(C).
The 200 amp breaker is fine for the primary protection.
 

d0nut

Senior Member
Location
Omaha, NE
I could be wrong about the center tap, this is the older service now fed from the new 480 service, they have a 300kva 480v delta to 240v/120v delta transformer feeding a main 240 3phase 3wire distribution panel, then out to the older service. All of the older main service is fed only with 3phase 3wire (no neutral) and its original labeling says 3pahse 3wire, so again I may be wrong, that's why I'm here asking for help. I do like your suggestion.
It may also make more sense to feed your new transformer from the 480V service if the plant is trying to move away from the old 240V equipment they have. That way you aren't adding new loads to a system they are trying to remove.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thats what I originally wanted to do, but when I opened the main panel, it lacks the neutral. All of the older 208v/120v panels have a 240v delta to 208v/120v transformer feeding the 208v120v panels.
I plan to come off the spare 200a breaker from the 240v delta panel, install a 75KVA 240 delta to 208v/120v wye transformer to feed the new power panel
If the 75 Kva works for you then just go with that.
 

jeff motta

Member
Location
nj
Occupation
electrician
It may also make more sense to feed your new transformer from the 480V service if the plant is trying to move away from the old 240V equipment they have. That way you aren't adding new loads to a system they are trying to remove.
I agree, I threw that out there but they are limited on 480v distribution and want to save any open space for future machines.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I agree, I threw that out there but they are limited on 480v distribution and want to save any open space for future machines.
Another possibility if they don't have any older 120V loads that are voltage sensitive like incandescent lighting, is remove the 240 delta and replace it with a 220Y127 (you possibly could use a 208Y120 with a tap changer). The 220 would be likely high enough for the 240V equipment, and VFD's like a wye type voltage better than delta.
You would probably save about 3000kwh a year in transformer losses.
 