an indoor hot tub has a 120v heater and a 120v pump, each with its own plug in cord. they are plugged into outlets that are fed from a 240v gfci circuit breaker. is this to code?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
an indoor hot tub has a 120v heater and a 120v pump, each with its own plug in cord. they are plugged into outlets that are fed from a 240v gfci circuit breaker. is this to code?

If this is a multiwire branch circuit-- 2 hots, neutral and a ground and the receptacles are sharing the neutral then a DP GFCI is necessary in order for it to function properly.
 