I am working on a remodel of an existing building with 240/3 phase/4 wire high leg service. The old use was an office/retail, the new use will be a gym. The old service will remain, but we will be adding a lot of single phase in the way of treadmills and stair climbers, etc. My question is in the resulting imbalance of the phases. The high leg will only run the rooftop units, which at full connected load (summer AC running) is only 25% of the total load. In the winter, the 3 phase load will be much less. I have seen a number of these types of set ups, where the phases are unbalanced, and everything is fine, but the thing that bothers me is the magnitude of the imbalance due to the single phase exercise equipment. Is this a case where I should worry about the HVAC motors burning out due to the imbalance, and therefore ask for a transformer (240/3 to 208/3) to provide a more balanced 3 phase load?
The new service for the space will actually be smaller. The old CT was 1100A, our new one is 800A. And they are reusing the rooftop units which will remain 3 phase.
Thanks in advance for any direction.
The new service for the space will actually be smaller. The old CT was 1100A, our new one is 800A. And they are reusing the rooftop units which will remain 3 phase.
Thanks in advance for any direction.