RFEngineer
Member
Just when I need my 2008 NEC book, it eludes me...
I presently have a branch circuit with 10/4 cabling, a 30A double-pole breaker, and a 30A L14-30R (250V/125V) receptacle that serves an electronic equipment rack. 30A is well over-rated for the acrtual use. I am going to start using a UL-compliant 240V RPT that is limited to 20A connectors per UL RPT guidelines. Here's my question:
If I change the serving wall receptacle to a single 20A L14-20R, must the serving breaker also be rated 20A or may I leave the existing 30A breaker? My gut tells me NEC will require alignment of a 20A breaker for use with a single 20A receptacle. Gut right or wrong? Tnx!
Paul
I presently have a branch circuit with 10/4 cabling, a 30A double-pole breaker, and a 30A L14-30R (250V/125V) receptacle that serves an electronic equipment rack. 30A is well over-rated for the acrtual use. I am going to start using a UL-compliant 240V RPT that is limited to 20A connectors per UL RPT guidelines. Here's my question:
If I change the serving wall receptacle to a single 20A L14-20R, must the serving breaker also be rated 20A or may I leave the existing 30A breaker? My gut tells me NEC will require alignment of a 20A breaker for use with a single 20A receptacle. Gut right or wrong? Tnx!
Paul