I recently had another electrical contractor contact me about a problem he was having with an HVAC contractor. The HVAC contractor had all but called him an idiot, and he called me to get a second opinion before he argued with him further. The job involved hooking up condensing units that were only 240V single phase units, but the service they were being connected to was a 3 phase Delta service with the 208V wild leg. The units are 240V only, with no 120V connection at all. According to the HVAC contractor the units would not run if one of the 2 lines of the condensing unit was tied to the wild leg (even though the voltage at the unit would still just be 240V), and advised the building owner that he would not warranty the units if problems would arise if they were hooked up that way. The only problem we could come up with was that if something was to go to ground in the compressor it would put the higher voltage to ground if that leg was the wild leg, but at that point it wouldn't really matter since if something had gone to ground inside the compressor it would probably be shot at that point anyway.
An engineer from the power company also met with him and the building owner and could not see any reason why the compressors would not run correctly when one leg was tied to the wild leg.
We tried to find any code references prohibiting the use of the wild leg on condensing units, but were unable to. To us it made more sense and helped balance the load by using all 3 connection possibilities for all of the units.
An engineer from the power company also met with him and the building owner and could not see any reason why the compressors would not run correctly when one leg was tied to the wild leg.
We tried to find any code references prohibiting the use of the wild leg on condensing units, but were unable to. To us it made more sense and helped balance the load by using all 3 connection possibilities for all of the units.