Alright.. here is a fun one.
Without going to into mass detail.... We have a 240V SINGLE phase step up to 480v SINGLE phase transformer. 2017 NEC 250.20(B) says...
And NEC 250.30(B) says...
By our understanding... because we are above 150V to ground... and because we are an ungrounded system with no GROUNDED conductor on the secondary side... do we need to provide a GROUNDING electrode conductor to the system? We do plan on carrying an EQUIPMENT grounding conductor to the transformer... but is the additional grounding required?
Without going to into mass detail.... We have a 240V SINGLE phase step up to 480v SINGLE phase transformer. 2017 NEC 250.20(B) says...
And NEC 250.30(B) says...
By our understanding... because we are above 150V to ground... and because we are an ungrounded system with no GROUNDED conductor on the secondary side... do we need to provide a GROUNDING electrode conductor to the system? We do plan on carrying an EQUIPMENT grounding conductor to the transformer... but is the additional grounding required?