Hello all.
So i have a question about sizing a split phase xfmer. I need to upsize it to swap in some larger ultrasonic generators. Currently i have a 480VAC to 240V phase to phase xfmer rated for 10KVA powering (4) 1200W ultrasonic generators. Currently our fuse sizing is follows, 30A FNQ-R class CC as Pri. protection, 30A breaker Sec. protection and 10A for each generator. Do I treat this as a Single phase transformer and use NEC450.3B and fuse table 240.6A? or is there a special setup I need to use for a proper calculation.
Well after some testing we need to upsize the generators to 2600W a piece. Real quick math is saying we are now at 10.4KVA for the generators alone (each one drawing 10.83A for 43.32A total) (excludes the two 5A 120V outlets for the computers) and the xfmer should be upsized to the 15KVA. I believe i can get away with a 63A breaker for the collective generator breaker and use 15A breakers for the individual generator breakers. For the Pri. side I believe I can go as large as a 70A, but i think a 45A would be fine since that should 150% of FLA for the xfmer.
Thanks everyone.
So i have a question about sizing a split phase xfmer. I need to upsize it to swap in some larger ultrasonic generators. Currently i have a 480VAC to 240V phase to phase xfmer rated for 10KVA powering (4) 1200W ultrasonic generators. Currently our fuse sizing is follows, 30A FNQ-R class CC as Pri. protection, 30A breaker Sec. protection and 10A for each generator. Do I treat this as a Single phase transformer and use NEC450.3B and fuse table 240.6A? or is there a special setup I need to use for a proper calculation.
Well after some testing we need to upsize the generators to 2600W a piece. Real quick math is saying we are now at 10.4KVA for the generators alone (each one drawing 10.83A for 43.32A total) (excludes the two 5A 120V outlets for the computers) and the xfmer should be upsized to the 15KVA. I believe i can get away with a 63A breaker for the collective generator breaker and use 15A breakers for the individual generator breakers. For the Pri. side I believe I can go as large as a 70A, but i think a 45A would be fine since that should 150% of FLA for the xfmer.
Thanks everyone.