AWinston:
I have a DeWalt radial arm saw. Single phase 120 or 240 and something over 1 HP possibly 1.5 HP. Installed was a 10 or 12 inch blade.
This was wired 120 V, and was in a location with about 120 ft of #12 copper Romex from a 20 A QO in the main panel. On startup it drew 80 A or so for a number of seconds, I believe about 5 seconds before reaching speed. A short time, a few seconds, possibly 10 or 15, if a restart was tried the QO would blow. To be expected.
If this same Romex had been supplied with 240 the motor would have started very quickly. It wasn't really Romex, but rather #12 in conduit, but Romex was a good way to indicate the wire length.
If the saw is much closer to the main panel with a shorter run of wire, then it starts with a second.
Why not rewire the saw for 240. Because the saw can be moved around and 120 is available almost anywhere.
.