240VAC vs 208V

Status
Not open for further replies.

Suyash599

Member
Location
North Brunswick, NJ
Occupation
PV Design Engineer
Hey guys!

I am looking at a gear setup that is 208V rated all panelboards and transformer secondary.

Hot sequence, no CTs, no main breaker. The fused service disconnect switch is rated @ 240VAC and 250VDC?

What does this mean? Service is 208V or 240V?
 
Very likely all of the breakers and disconnects are rated for 240V (or higher) even though they are only being used at 208V.

The wire insulation is probably rated for 600V.

-Jon
 