Hi All
I am trying to properly size a 120/240 secondary transformer fuses... The current fuses are un readable due to age... I have a 240 open delta system with center tap grounded at the pole, A 3 kva 240 volt primary to 240 volt with neutral secondary transformer was installed to keep the single phase panel volts from floating all over the place... Particularly line to neutral
Obviously this is an old (1949) system. I want to make sure the fuses are properly sized for safety sake and piece of mind. As we all know, if a 15 amp fuse blows...obviously we need a 30...
so who knows what some good intentioned person put in circuit...
Question 1. Does it matter what 2 phases the single phase transformer is connected to? (it has a wild leg, which is not meaningful line to line... But will the center tap to ground effect anything?)
Question 2, Fuse sizing... it is a 3 kva single phase transformer... I'm thinking 30 amps per phase on the primary and 15 amps per phase on the secondary.. am I correct?
Thanks for any input