Old client calls me, can I bring a new SA circuit from the main to the adjoining area to the kitchen. Its a condo conversion for her parents.
There is a narrow counter there and it looks like it is missing layout.
I go there and find a fairly good looking electrical job.
But it doesn’t really look like the counter is exactly part of the kitchen.
And I find another outlet 10’ away that looks like the installer believed he was laying out for the 6-12/12-6 layout.
He didn’t really miss anything else as far as I could see. But the counter does look a little like its missing one.
I know the inspector and he really doesn’t want to be unreasonable.
How to present my case that the counter doesn’t need another outlet from the mains?
There is ample power in the kitchen. The family is on a fixed income…
In the kitchen there are 8 cts
- 2 SA cts;
- Disp
- dw;
- hood circuit [great for MW];
- IA refer;
- IA ignitor!;
- and a general lighting
The counter in question is too narrow to prepare food, there is no 24" cabinet beneath.
Its really only used for papers and his diabetic needles. Its got a narrow cabinet below
210.52(A)(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets that do not have countertops or similar work surfaces
So the kitchen has ample power. The counter would make layout on 6 12 12 6
The nearby counter in the open floor plan I would characterize as not being part of the kitchen.
210.52(C) Countertops and Work Surfaces. In kitchens, pantries, breakfast rooms, dining rooms, and similar areas of dwelling units, receptacle outlets for countertop and work surfaces shall be installed in accordance with 210.52(C)(1) through (C)(5).
That counter makes a wall layout of 12’ with the outlet at hammer height.
The counter outlet is a combo switch on the general lighting ct, so it is at elbow height which should be ok as per
210.52 Dwelling Unit Receptacle Outlets. This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:
(1) Part of a luminaire or appliance, or
(2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1, or
(3) Located within cabinets or cupboards, or
(4) Located more than 1.7 m (5½ ft) above the floor
https://iaeimagazine.org/2009/july2009/dwelling-units-no-big-dealright/
The enforcing agency often has to use good judgment and discretion relative to making this determination to ensure that adequate circuitry and receptacle outlets are provided for the anticipated use.
How to present my case that the intention of the installer was to layout on 6 12 12 6 and that 2 44 2 is not the intention of the installer w regards to this adjacent counter? Thanks guys!