ptonsparky
Tom
- Occupation
- EC - retired
New customer via a pump installer that sends me "opportunities" on occasion.
An external power supply for a transducer to his well VFD fails about once a year. He pointed it out to me thru the ventilation slots in the VFD. Sure enough a RH___ power supply directly connected to L3 of the VFD and the EG. Lead length may be 6" of #14. L3 is the hi leg of a 240 Delta. Approx 212 volt to grnd. The supply is rated 100-240AC. I have used these power supplies and have yet to have a failure. Could the proximity to the vfd be a factor, the high leg in general or both?
Why the external power supply? Don't know. I was to befuddled as to who and why anyone would hook up a power supply the way they did.
An external power supply for a transducer to his well VFD fails about once a year. He pointed it out to me thru the ventilation slots in the VFD. Sure enough a RH___ power supply directly connected to L3 of the VFD and the EG. Lead length may be 6" of #14. L3 is the hi leg of a 240 Delta. Approx 212 volt to grnd. The supply is rated 100-240AC. I have used these power supplies and have yet to have a failure. Could the proximity to the vfd be a factor, the high leg in general or both?
Why the external power supply? Don't know. I was to befuddled as to who and why anyone would hook up a power supply the way they did.