I have a 24 volt dc, 2.5 amp, power supply. Does the NEC allow me to run these 24v dc wires in the same conduit with #12 AWG, 120v ac, conductors? Or must they be in separate conduits?
Code references would be appreciated. Thanks.
In general the answer is they can occupy the same raceway.
The size of the AC wires is not an issue.
300.2 (C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less.
Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
However, it is possible the 24V wires (or even the 120V wires) are part of a limited energy circuit. You are not usually allowed to run limited energy circuits in the same conduit as non-limited energy circuits. Article 725 covers limited energy circuits, but it is written so poorly that it is not readily understandable.
If this is part of an industrial machine, NFPA79 rules would apply, which tend to be less restrictive than NEC rules.