I've looked in art 450 and art 240. I cannot find an exemption for secondary conductor OCP for door bell transformers.
The door bell conductors run typically is longer than 10 ft 240.21(C)(2)(1)a.(?)
Table 450.3(B) note 2. implies secondary conductor protection, therefore leading me back to Art. 240.
Can someone tell me a code reference to avoid installing an in-line fuse holder with a glass 250 VAC 1 amp fuse for doorbell wiring.