What section of the NEC deals with 24VDC and 120VAC when is comes to the two being in the same conduit or if it is even allowed?
The application is I/O for automation and the conduit/pipe is from enclosure to enclosure.
Thanks
I knew there was a online NEC but now it appears you have to resister so I can't read that right now.
infinity:300.3(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 600 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
Exception: For solar photovoltaic systems in accordance with 690.4(B).
FPN: See 725.136(A) for Class 2 and Class 3 circuit conductors.
725.136 Separation from Electric Light, Power, Class 1, Non?Power-Limited Fire Alarm Circuit Conductors, and Medium-Power Network-Powered Broadband Communications Cables.
(A) General. Cables and conductors of Class 2 and Class 3 circuits shall not be placed in any cable, cable tray, compartment, enclosure, manhole, outlet box, device box, raceway, or similar fitting with conductors of electric light, power, Class 1, non?power-limited fire alarm circuits, and medium-power network-powered broadband communications circuits unless permitted by 725.136(B) through (I).
(B) Separated by Barriers. Class 2 and Class 3 circuits shall be permitted to be installed together with the conductors of electric light, power, Class 1, non?power-limited fire alarm and medium power network-powered broadband communications circuits where they are separated by a barrier.
(C) Raceways Within Enclosures. In enclosures, Class 2 and Class 3 circuits shall be permitted to be installed in a raceway to separate them from Class 1, non?power-limited fire alarm and medium-power network-powered broadband communications circuits.
(D) Associated Systems Within Enclosures. Class 2 and Class 3 circuit conductors in compartments, enclosures, device boxes, outlet boxes, or similar fittings shall be permitted to be installed with electric light, power, Class 1, non?power-limited fire alarm, and medium-power network-powered broadband communications circuits where they are introduced solely to connect the equipment connected to Class 2 and Class 3 circuits, and where (1) or (2) applies:
(1) The electric light, power, Class 1, non?power-limited fire alarm, and medium-power network-powered broadband communications circuit conductors are routed to maintain a minimum of 6 mm (0.25 in.) separation from the conductors and cables of Class 2 and Class 3 circuits.
(2) The circuit conductors operate at 150 volts or less to ground and also comply with one of the following:
a. The Class 2 and Class 3 circuits are installed using Type CL3, CL3R, or CL3P or permitted substitute cables, provided these Class 3 cable conductors extending beyond the jacket are separated by a minimum of 6 mm (0.25 in.) or by a nonconductive sleeve or nonconductive barrier from all other conductors.
b. The Class 2 and Class 3 circuit conductors are installed as a Class 1 circuit in accordance with 725.41.
725.136 Non–Power-Limited Fire Alarm Circuit Conductors, and Medium-Power Network-Powered Broadband Communications Cables.
I don't think this is applicable?
725.127 Wiring Methods on Supply Side of the Class 2 or Class 3 Power Source.
Conductors and equipment on the supply side of the power source shall be installed in accordance with the appropriate requirements of Chapters 1 through 4. Transformers or other devices supplied from electric light or power circuits shall be protected by an overcurrent device rated not over 20 amperes.
Exception: The input leads of a transformer or other power source supplying Class 2 and Class 3 circuits shall be permitted to be smaller than 14 AWG, but not smaller than 18 AWG if they are not over 12 in. (305 mm) long and if they have insulation that complies with 725.49(B).
725.136 Non?Power-Limited Fire Alarm Circuit Conductors, and Medium-Power Network-Powered Broadband Communications Cables.
I don't think this is applicable?
24vdc I/O is neither Non?Power-Limited Fire Alarm Circuit Conductors or Medium-Power Network-Powered Broadband Communications Cables.
Infinity,
I have 2008 NEC - I read 725.127 Wiring Methods on Supply Side of the Class 2 or Class 3 Power Source.
BUT....
Take a look at the FPN
"See 725.55(A) for Class 2 and Class 3 circuit conductors."
Sorry, quoted the wrong article
Sorry I listed the wrong code section.
How do Generac generators get away with having the 12v control and 240v sense wires in the same 4-conductor bundle?
That could be a Class 1 control circuit and would be permitted in with directly associated power conductors.How do Generac generators get away with having the 12v control and 240v sense wires in the same 4-conductor bundle?
There is no 725.55(A).
That could be a Class 1 control circuit and would be permitted in with directly associated power conductors.
Rob
I am surprised at your answer.
My response is based on the 2005 NEC.
It is 725.136(A) in the 2008 NEC if that keeps ya happy.
I think for most of us on the forum we left the 2005 behind quite some time ago.![]()