I am wondering if one can run a 24Vdc Rapid Shutdown switch supply cable in the same conduit as AC cables (coming out of my inverters).
Here is my thinking process:
1) In general, we can make DC and AC work together code-wise per 303.3(C), it's not good field practice from what I've seen on this forum but it's code-compliant provided insulation is upgraded.
2) However, since this 24Vdc is not just a DC cable, but a DC power source for a switching device (Rapid Shutdown), it is a Class 2 cable. We then need to turn to NEC 725.136 which overrides 300.3(C).
3) 725.136(A) tells me that I can't mix Class 2, 3 with Class 1 in the same tray, enclosure...unless permitted by (B) through (I).
4) I turn to permission (D)(2) to reclassify my 24Vdc Class 2 cable into a Class 1 per 725.41.
Does it make sense ? Where do I go from there anyway ? How do I apply 725.41 to reclassify my Class 2 24Vdc cable into a Class 1 ?
Thanks!
I am wondering if one can run a 24Vdc Rapid Shutdown switch supply cable in the same conduit as AC cables (coming out of my inverters).
Here is my thinking process:
1) In general, we can make DC and AC work together code-wise per 303.3(C), it's not good field practice from what I've seen on this forum but it's code-compliant provided insulation is upgraded.
2) However, since this 24Vdc is not just a DC cable, but a DC power source for a switching device (Rapid Shutdown), it is a Class 2 cable. We then need to turn to NEC 725.136 which overrides 300.3(C).
3) 725.136(A) tells me that I can't mix Class 2, 3 with Class 1 in the same tray, enclosure...unless permitted by (B) through (I).
4) I turn to permission (D)(2) to reclassify my 24Vdc Class 2 cable into a Class 1 per 725.41.
Does it make sense ? Where do I go from there anyway ? How do I apply 725.41 to reclassify my Class 2 24Vdc cable into a Class 1 ?
Thanks!