24VDC wiring between individual control cabinets.

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Construction requests to wire from cabinet to cabinet (3 total, side by side) with 24VDC discreet and 4-20mA analog circuits (no power). The client prefers to see individual conduit penetrations into each cabinet rather than a 'wiring-through' scenario, but I cant see how this is a safety issue if the wiring does not contain power from a second source and doesnt terminate there. Is there any violation here?
 
While I agree no safety issue, there could be a physical issue. Suppose cabinet 2 of 3 needs to be replaced. Perhaps the client does not realize that the individual components can be replaced and the back box will always remain.
 