Can you run 24vdc circuits in the same cable as 110. We are using cable rated for 600 volts like an IMSA rated 9 conductor awg 14. I have been told by our local inspector that it's ok if the cable is rated for the AC.
You need to check the classification of the 24 volt circuit. A class 2 or class 3 circuit can not be in the same cable as 120 volt power circuits. Look at 725.55.
You need to check the classification of the 24 volt circuit. A class 2 or class 3 circuit can not be in the same cable as 120 volt power circuits. Look at 725.55.