We were called to a job today for one of our regular customers who manages several apartment buildings.
One of their tennants had called POCO to have them install an energy management device on the water heater in their apartment. POCO's electrical subcontractor had refused to connect the EMD because of what he claimed was a code violation.
The building has a 3 phase Wye service ( 120/208 Volts ), the water heater nameplate said 4500 Watts @ 240 Volts, the heater was wired with # 10 TW ( only 2 conductors in 1/2 inch EMT), and on a 30 Amp breaker. The POCO sub said it had to be changed to a 25 Amp breaker to be code compliant.
I don't know why and wondered if anyone here could explain it to me.
If I'm using Ohm's Law right, I come up with a 3380 Watt 16.25 Amp at 208 Volt load.