25 amp circuit with 20 amp plug/receptacle
acolella
Engineering Technician
I have some portable refrigerant recovery machines that were just purchased. These are 115V machines. The nameplate doesn't have a clearly defined MCA and MOCP. It just says Min Ckt: 20 Amp and Max Ckt: 25 Amp.
It has a 2 HP compressor motor with an FLA of 20 amps and a condenser fan motor with an FLA of 2.5 amps. The control box has built into it a NEMA L5-20P plug. It was shipped with a 50 foot 3/C 12 AWG SO cord with a NEMA L5-20R receptacle on one end and nothing on the other end. We installed a NEMA 5-20P plug on the other end.
When plugged into a receptacle on a 20 amp circuit with nothing else on the circuit, there were two instances when the breaker for that circuit tripped. I didn't have a practical way of measuring current at the time. I'm hoping to get to that tomorrow.
We are considering installing dedicated circuits/receptacles where these machines are going to be used. Since the machine was being fed from an essentially dedicated circuit and still tripped the breaker, I'm concerned that we are going to see more tripping, even with a 20 amp dedicated circuit.
My question is about the "Max ckt: 25 Amp" that is on the nameplate. Would it be acceptable to install circuits with 25 amp breakers, 10 gauge wire, NEMA 5-30R receptacles and NEMA 5-30P plugs on the cords? Or, can we not do this because of the NEMA L5-20P plug that is built into the control box of the machine?
I'm also wondering about the minimum and maximum ampacities on the nameplate. Normally, the MCA would be determined by the FLA of the compressor and condenser fan motor. 20 amps x 1.25 + 2.5 amps = 27.5 amps. Although, this is a portable cord connected appliance and I don't have experience with how the numbers are calculated for those. I'm not sure if these would normally even have an MCA or MOCP. It still seems like 20 amps, or even 25 amps, is a bit low for this machine.
I appreciate any replies. Thanks!
Compressor HP ratings are usually somewhat bogus. According to table 430.248 @115 volts a 2 HP motor has a FLC of 24 amps.
Did it trip upon starting or after it had been running for awhile?
Yeah, marketing decides the numbers and then they have to invent their own formulas to make it all work out. Damn things make a lot of heat too so you know they aren't anything near efficient. But they are cheap, available, and will do about 50% of what it says on the box
so i would be curious to see what min/max and sustained readings are on this recovery machine. if actuals are higher than advertised, then would a rewire or manufacturer warranty repair be in order? was the derated wire and plug/receptacle an accidental oversight? can you request for factory upgrade with minimums of 10 Ga wire and nema 5-30p and 5-30r?
Sent from my SM-S938U1 using Tapatalk
If the plug is 20 amps then the receptacle has to be 20 amps. You cannot use a 25 amp OCPD on a 20 amp receptacle.
Sounds like this could be considered as hvac equipment.
Why couldn't you wire to nameplate just like it says?
I will try to get some min/max and sustained currents along with voltage measurements the next time we need to use the machine. We haven't needed to use any of the machines since my initial post.
This is exactly what I would do. Since the other end of the cord is part of the (hopefully listed) machine, it should not enter into the discussion.
It is a listed machine. The plug that is built into the control box along with its receptacle on the cord was most likely determined as being safe and acceptable during testing. Didn't exceed temperature maximums, etc. It being a listed machine and having a nameplate specifying a maximum 25A circuit, I think we should be ok installing 25 amp dedicated circuits for these machines.