25 foot rule for transformers

Merry Christmas
Status
Not open for further replies.

KP2

Senior Member
Location
New Milford, CT
In the Handbook Ex.240.9 Shows the Secondary to primary Ratio of 208/480 = .433. In 240.21(B)(3)(2) it says to use the Primary to secondary ratio. the way we see it the calculation schould go like this; 480/208=2.308. 2.308*36.667 = 84.627 amps. The 36.667 is one third of the OCPD of the primary.

In conclusion the secondary Tap conductor shall not be smaller than 84.627 amps. which would be a # 3 out of the 60 deg C column. If we use the .433 it tells us the smallest wire is 15.877 amps rated. :confused::confused::confused:
 
never mind

never mind

Nevermind I'm From CT and we are still using the 05. I looked in the 08 and it is as we read it 2.31.
Sorry Always check the latest edition right.:D
 