That's true for 240.21(C)(6) but doesn't appear to be true for 240.21(C)(3), which I understand the subject to be referring to.
Cheers, Wayne
You have a point. I never got to use that section before.
View attachment 2569550
This shows no MCB is needed
Sent from my iPhone using Tapatalk
Might be legit. Do you meet all the criteria?
(3) Industrial Installation Secondary Conductors Not Over 7.5 m (25 ft) Long
For the supply of switchgear or switchboards in industrial installations only, where the length of the secondary conductors does not exceed 7.5 m (25 ft) and complies with all of the following:
Conditions of maintenance and supervision ensure that only qualified persons service the systems.
The ampacity of the secondary conductors is not less than the secondary current rating of the transformer, and the sum of the ratings of the overcurrent devices does not exceed the ampacity of the secondary conductors.
All overcurrent devices are grouped.
The secondary conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.