25 foot XFMR secondary conductors 240.21(3)

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
If my transformer secondary conductors are 25’ or less to the switchboard, do I really need a MCB? Can I use 6 disconnects in lieu of the Main if all other conditions are met?


Sent from my iPhone using Tapatalk
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
That's true for 240.21(C)(6) but doesn't appear to be true for 240.21(C)(3), which I understand the subject to be referring to.

Cheers, Wayne
You have a point. I never got to use that section before.
View attachment 2569550
This shows no MCB is needed


Sent from my iPhone using Tapatalk
Might be legit. Do you meet all the criteria?

(3) Industrial Installation Secondary Conductors Not Over 7.5 m (25 ft) Long
For the supply of switchgear or switchboards in industrial installations only, where the length of the secondary conductors does not exceed 7.5 m (25 ft) and complies with all of the following:
Conditions of maintenance and supervision ensure that only qualified persons service the systems.
The ampacity of the secondary conductors is not less than the secondary current rating of the transformer, and the sum of the ratings of the overcurrent devices does not exceed the ampacity of the secondary conductors.
All overcurrent devices are grouped.
The secondary conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
That's true for 240.21(C)(6) but doesn't appear to be true for 240.21(C)(3), which I understand the subject to be referring to.

Cheers, Wayne

I should have mentioned I was looking at the 2017 NEC


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
You have a point. I never got to use that section before.

Might be legit. Do you meet all the criteria?

(3) Industrial Installation Secondary Conductors Not Over 7.5 m (25 ft) Long
For the supply of switchgear or switchboards in industrial installations only, where the length of the secondary conductors does not exceed 7.5 m (25 ft) and complies with all of the following:
Conditions of maintenance and supervision ensure that only qualified persons service the systems.
The ampacity of the secondary conductors is not less than the secondary current rating of the transformer, and the sum of the ratings of the overcurrent devices does not exceed the ampacity of the secondary conductors.
All overcurrent devices are grouped.
The secondary conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.

Yes sir. The installation would meet all this criteria.


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
What about 408.36 ???
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
What about 408.36 ???
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
That only applies to panelboards, it does not apply to switchboards or switchgear. The OP specified a switchboard.
 

zooby

Member
Location
Indiana
Occupation
maint. electrician
You have a point. I never got to use that section before.

Might be legit. Do you meet all the criteria?

(3) Industrial Installation Secondary Conductors Not Over 7.5 m (25 ft) Long
For the supply of switchgear or switchboards in industrial installations only, where the length of the secondary conductors does not exceed 7.5 m (25 ft) and complies with all of the following:
Conditions of maintenance and supervision ensure that only qualified persons service the systems.
The ampacity of the secondary conductors is not less than the secondary current rating of the transformer, and the sum of the ratings of the overcurrent devices does not exceed the ampacity of the secondary conductors.
All overcurrent devices are grouped.
The secondary conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.
man...that second condition is a tough one if I am reading that correctly. I just happen to be floating this idea here but were are not true industrial and I believe a fused disco would help ( here ) with sccr.
 